I attach CPU diagnose. Pease help.
AttachmentDiagnose_171116.txt (453 Downloads) |
3/19/2021 10:52 AM | |
Joined: 10/28/2019 Last visit: 6/30/2024 Posts: 1 Rating: (0) |
What is the solution for these errors ? [snip]
AttachmentDiagnosticBuffer.txt (404 Downloads) |
Last edited by: Jen_Moderator at: 03/19/2021 13:10:58Added diagnostic buffer as txt. file. |
|
3/19/2021 11:17 AM | |
Joined: 9/27/2006 Last visit: 10/17/2024 Posts: 12289 Rating: (2687)
|
Hello freak; Before we go on with an answer to your question, posting the contents of your diagnostic buffer inside a post makes reading it difficult for us. Next time, it would be better to insert the diagnose.txt file as as attachment (see the "Add Attachment" button below your post). We can then open it outside of the forum and use external tools to examine the contents. One message is recurrent in many entries if your diagnostic buffer: "Requested OB: I/O redundancy error OB (OB70) OB not found, or disabled, or cannot be started in the in the current operating mode" Please read the important note from the S7-400H manual, regering to diagnostic OBs that must be included in a S7-400H program. It might not fix all the problems in your configuration in one shot, but your systrm will not go down due to OB-covered events, and the diagnostic buffer will present more precise information on the cause of faults im your system. https://support.industry.siemens.com/cs/ww/en/view/82478488/29194024331 Hope this helps, Daniel Chartier |