5/4/2017 7:48 PM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hi, 1.) no this error have nothing to do with CPU Usage 2.) depends from which version to which version(if you change the Mainversions you need new Scout and some changes on the project) 3.) normally not 4.) Latest FW ist V4.5.0.3 https://support.industry.siemens.com/cs/ww/en/view/109746842 Which FW Version of the D425 you use at the moment? Regards Christoph |
This contribution was helpful to1 thankful Users |
5/4/2017 8:37 PM | |
Joined: 11/17/2010 Last visit: 5/16/2024 Posts: 104 Rating: (2) |
Hi
|
Last edited by: esantos at: 5/4/2017 11:00:06 PMBest regards, |
|
5/5/2017 6:02 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, you can only update to V4.3 HF25, that is the latest FW Release for your type of D425. The V4.5 FW ist only available for the newer Simotion D4xx-2! It can be that this error is fixed in the last Version of V4.3 for the PLC but to check that you should open a Service Request to get a detailed analyze from Siemens Development for this error.
Christoph |
7/13/2017 12:02 PM | |
Joined: 6/19/2017 Last visit: 5/16/2024 Posts: 8053 Rating: (164) |
New question published by LALU HCMX is split to a separate thread with the subject Why goes Simotion CPU to stop mode? . Best regards |
My Forum is the place to personalize your profile, |
|