6/28/2015 1:40 PM | |
Joined: 5/28/2008 Last visit: 8/6/2024 Posts: 4515 Rating:
|
Hello, Did you tried to use the totalizer FC from the following link? How can you accumulate physical flow measurements (e.g. mass flow rate, flow velocity) to an overall value? |
Ayman Elotaify |
|
This contribution was helpful to
1 thankful Users |
6/29/2015 3:44 AM | |
Joined: 10/7/2005 Last visit: 8/9/2024 Posts: 3016 Rating:
|
Hello sacheen your problem is caused by trying to add a very small amount to an ever increasing large Floating Point number. (32bit) Floating Point numbers accuracy is limited to about 6 decimals and you are now reaching this limit (have a look too at https://support.industry.siemens.com/cs/document/14844391/how-accurately-can-i-calculate-with-real-numbers-that-are-used-in-extensive-formulas? for more on this). As far as I'm concerned, the one and only accurate totalising way is to use a digital pulse output from your flow meter, connect it to DI, set the flow meter to output a pulse for lets say each full m3 and accumulate this as a DINT value. I hope this helps |
Last edited by: fritz at: 6/29/2015 3:46:22 AMfixed FAQ link Cheers |
|