Dear All, Will anybody provide me the procedure to Force Failsafe Digital I/O's of SM-326 |
6/19/2013 8:43 PM | |
Joined: 9/27/2006 Last visit: 11/18/2024 Posts: 12296 Rating: (2691)
|
Hello nishu; The answer to your question is quite easy. From the manual:SIMATIC Industrial Software S7 Distributed Safety - configuring and programming Modifying Values in F-DBs Values in F-DBs can only be modified online in the F-CPU. If the value is also to be changed offline, you must do this by editing the actual value and compiling the safety program offline, as well.Modify only the parameters described in this documentation. Additional Rules for Testing · Forcing is not possible for F-I/O. · Setting breakpoints in the standard user program will cause the following errors in the safety program: – Expiration of F-cycle time monitoring – Error during communication with the F-I/O – Error during safety-related CPU-CPU communication –Internal CPU faults Hope this helps, |