4/16/2020 8:25 AM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (296) |
Hi, ok I see. This is the simple limit switch function with speed control, not EPOS (my picture before) See this manual chapter 6.11: https://support.industry.siemens.com/cs/de/en/view/109757229 The function is explained here quite good with timing diagram as well. Of course you can try this out only in online mode with the drive. r3344 will be changed by the runtime, not offline by the engineering tool. So with p3340 you start the motion -> the direction of motion is defined by the speed setpoint (positve speed setpint = positive movement if p1113 = 0, otherwise vice versa). With p3342 and p3343 you wire your limit switches - please note that they are low active switching! |
Best regards, |
|
This contribution was helpful to1 thankful Users |
4/16/2020 8:01 PM | |
Posts: 36 Rating: (3) |
Hi Robert, very useful indeed. Yesterday I was trying at home but this morning I've been able to test it online and it does work. Thanks for your kind help. Regards, |
This contribution was helpful to1 thankful Users |
2/12/2024 9:28 AM | |
Joined: 7/26/2023 Last visit: 2/12/2024 Posts: 1 Rating: (0) |
Which parameter have you used for interconnection at "Limit switch Start"? Is it r1198? |
Last edited by: Zakanzulya at: 02/12/2024 09:30:00 |
|