Instead of using SFC, how can we do it in SCL. I had a program in S7 1214C which i am migrating it to S7 412-2 PN (TIA portal v17.0.0.0) and i found out get_im_data block doesn't work for 412 CPU. So i am looking out for an alternative right now. My complete program is in SCL and i am not well verse with using SFC. Can you help? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/29/2022 06:18:48New subject after splitting |
|
12/1/2022 1:58 PM | |
Joined: 9/23/2005 Last visit: 11/12/2024 Posts: 4784 Rating: (730)
|
To get IM data on a S7-400 system you should use SFC 51 "RDSYSST". It can be used in the SCL language. Manual or search TIA Information System. |