Joined: 11/29/2011 Last visit: 9/26/2024 Posts: 1359 Rating: (232) |
Hi, Yes, it is possible to solve the issue. The solution is up to the alarming system you are using. Message numbering: For the understand the principle there is standard procedure to do it with PCS7 see the Buffering of Process Messages including Time Stamps with ALARM_7B example. Bit alarming: You need to take care of the Alarm trigger bits to be buffered until the connection restores.That takes some programming effort. If you have any further questions please do not hesitate to ask! |
- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to1 thankful Users |
4/8/2016 1:42 PM | |
Joined: 11/29/2011 Last visit: 9/26/2024 Posts: 1359 Rating: (232) |
Hi,
The demo project also contain the SCL source, so you could customize the block. I hope I could help! |
- What you read here, please check with manuals and your requirements. |
|
1/5/2018 11:15 AM | |
Joined: 9/1/2005 Last visit: 10/14/2024 Posts: 4109 Rating: (195) |
New question published by ANSHUMAN_SINGH is split to a separate thread with the subject Generate a communication fault Alarm in Hmi & wincc if PLC is disconnected. Best regards |