4/29/2014 2:43 PM | |
Joined: 5/22/2012 Last visit: 3/24/2022 Posts: 895 Rating: (67) |
Hello, if you use a S7-1500,you canuse the Technology Object there. So you would get the actual position directly inside the SIMATIC. You would work with PLC- Open blocks for positioning. If you have a S120, you can activate the basic positioner with standard telegramm 111. There is the actual position (r2521[0]) in the telegramm. For a easy communication you can use the function block SINA_POS ("FB286"): http://support.automation.siemens.com/WW/view/de/68034568 It would be also possible to activate the position controller standalone as function module (without basic positionier, if you only interrested in the actual position). Then you have to active the position controller by p2550 = 0 and have to reactivate the speed setpoints by p1142 = 1. Regards Zako |
Last edited by: zako_ at: 4/29/2014 8:52 PM |
|
4/29/2014 5:29 PM | |
Posts: 19 Rating: (0) |
Having problem downloading library which contains FB284 for TIA Portal. I am not from germany, can I download it? |
4/29/2014 5:42 PM | |
Joined: 8/31/2005 Last visit: 3/7/2024 Posts: 2197 Rating: (326) |
For STEP 7 V5 Download it from http://support.automation.siemens.com/WW/view/en/25166781 For TIA Portal use http://support.automation.siemens.com/WW/view/en/68034568 (You have to pass a export control check to download) |
|
|