Hell Ilya; The DP/PA coupler is completwly transparent to the DP master, you do not need a gsd file for it, and you do not configure it in the Profibus-DP network. You do need a gsd file for the PA-slave that will be connected through the DP/PA coupler (if it is not a Siemens PA slave, and has not been integrated in the Profibus configurator librairies). And the whole DP network must operate at 45.45/31,25 kB (you must set the parameters of the bus to that speed). See the following FAQ, in the section dealing twith a DP/PA coupler in standalone mode.. How do you set up the DP/PA link and how do you configure the DP/PA link and DP/PA coupler? What error do you see, and is there a message you could show us? Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 4/7/2015 6:36:35 PM |
|
4/9/2015 5:38 AM | |
Posts: 14 Rating: (0) |
Thank You so much for your respond. When I save and compile it shows this: Refer as picture attached. What do I need to do? |