12/9/2011 10:25 AM | |
Posts: 32 Rating: (1) |
Dear hac_am2003 I had the same problem.... Please note that a used MMC will be having information of old PLC.When yoyu insert it to another PLC, itwill try to read data from MMC which does not belong to it. That is why it continuosly blinks .... You need to format it and insert... Hope am correct... With Regards Pradeep Prabhu B |
12/18/2011 6:33 AM | |
Posts: 167 Rating: (4) |
Hi By MRES the "Actual values" will lost and change to "Initial values" on DBs. |
12/19/2011 3:49 PM | |
Joined: 7/15/2011 Last visit: 8/8/2024 Posts: 48 Rating: (0) |
Reply So it wont change the state of Mbits right? if i wanna to reset the mbits too, is there any possibilty? |
12/19/2011 6:47 PM | |
Joined: 3/21/2006 Last visit: 11/1/2024 Posts: 10229 Rating: (1181) |
No, basically will not reset M bits. But using start up OBs you can assign to that M bits some "initial' values like in How can you change the startup and actual values only via the OP in such a way as to be immune to power failure and general reset? Tips and tricks for calling and parameterizing SFBs, SFCs and IEC standard functions Best regards, Hristo Mihalev |