I have finished writing the logo Program for this application (attached ) there are 5 inputs to each logo and there are 4 logo so total 20 inputs from the HMI there will be 4 signals to be sent to Logo (Test lamp , Accept , Alarm Mute , Reset Alarm) i am attaching the Program and a sketch which explains everything , I have not worked on VM mapping before so i will need help on that . Attachmentlogo final.zip (298 Downloads) |
With kind regards... |
|
7/11/2017 11:01 AM | |
Joined: 12/18/2014 Last visit: 7/26/2024 Posts: 33419 Rating: (4147)
|
Is the programm in every LOGO! the same? |
7/11/2017 11:02 AM | |
Joined: 12/28/2016 Last visit: 12/22/2023 Posts: 364 Rating: (6) |
Yes same . |
With kind regards... |
|
7/11/2017 5:02 PM | |
Joined: 12/28/2016 Last visit: 12/22/2023 Posts: 364 Rating: (6) |
I mean to say even though the program is same there are 4 logo |
With kind regards... |
|
7/11/2017 5:48 PM | |
Joined: 12/18/2014 Last visit: 7/26/2024 Posts: 33419 Rating: (4147)
|
I have make for you a network project in which 4 LOGO!s 0BA8.Standard with the respectively same logic. Different in the programs there is only by the ranking of the commands from the HMI. In WinCC you have to connect to the LOGO! 1, for the other 3 LOGO!s, LOGO! 1 ranks the commands. The buttons for the commands to the respective LOGO! you must assign the following operands in WinCC:
AttachmentEngine_Alarm_1-4.zip (270 Downloads) |
This contribution was helpful to1 thankful Users |