You could convert your "102" from INT or REAL to DWORD and then assing each output with slice access. Info to slice access: https://support.industry.siemens.com/cs/ch/de/view/57374718/en Attachmentexample_bit.pdf (117 Downloads) |
Last edited by: MicTsc at: 3/20/2017 11:17:29 AM |
|
This contribution was helpful to1 thankful Users |
3/20/2017 11:18 AM | |
Joined: 11/16/2012 Last visit: 3/10/2024 Posts: 307 Rating: (52) |
An other example with byte slice access..
Attachmentexample_byte.pdf (119 Downloads) |
This contribution was helpful to1 thankful Users |
3/21/2017 10:23 PM | |
Joined: 3/23/2012 Last visit: 2/7/2024 Posts: 23 Rating: (0) |
I tried the program from MicTsc but but the PLC wont react at all. Do I have a mistake in it or do I mis something? AttachmentOB.pdf (78 Downloads) |
3/22/2017 10:57 AM | |
Joined: 11/16/2012 Last visit: 3/10/2024 Posts: 307 Rating: (52) |
Oh sorry, that was my fault. You have to start with Byte 3 in your DWORD. |