Hi to all.... I have a similar problem, and the same error. I'm have connected two s-1200 plc's with profinet. connected them as i-devices. I only set one output and pass it to the other plc. The communication is working when I download the project. But after the machine shuts down i get an error status on plc Error: User data failure of hardware component - Labeler / Labeler.Transfer area_1 but every thing is working. How can I reset this or avoid it? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/18/2017 1:25:10 PMNew subject after splitting |
10/23/2017 5:59 PM | |
Joined: 7/7/2010 Last visit: 8/9/2024 Posts: 15069 Rating:
Configure an OB for diagnostic error interrupt to have your PLC not halt on that type of error. There may be other options in the I-device configuration you may want to review as well that suit your specific process requirements. The F1-Help documentation may be more help than you expect....
science guy |