Dear friends EUREKA, I just tried to access to s71200 over internet and web server works great!!!! I sugest the following procedure: Step 1. Create a web server application and download it to S71200 Step 2. Testing web server application in LAN
Example: IP address of my PLC is 192.168.0.12 (Subnet mask 255.255.255.0., Router 192.168.0.1) I type in URL tab: http://192.168.0.12
Step 3. By Static IP address from your Internet provider,
Step 4. Router settings
(My router settings in attachments)
Step 5. Remote testing
(80 - port number) Step 6. ENJOY!!!... Dragan MarinkovicGreetings from Belgrade, Serbia
|
Be creative while inventing ideas and be disciplined while implementing them... :) |
|
This contribution was helpful to15 thankful Users |
3/15/2013 4:23 PM | |
Joined: 1/23/2009 Last visit: 7/20/2024 Posts: 29 Rating: (10) |
I tested again, and web server works... Today I tested two CPU-s: 1. CPU 1212C dc/dc/dc (6ES7212-1AE31-0XB0) - Firmware V3.0.1 2. CPU 1215C dc/dc/dc (6ES7215-1AG31-0XB0) - Firmware V3.0.1 I use simple router D-Link DI-524 If you wish to access only to default S71200 web page (not user define page), you just need to enable web server and you must correctly setup IP adresss, Subnet mask, Gateway(router adress) in PLC Properties. Also, you must correctly set the router as we have previously noted.... Best regards Dragan Marinkovic AttachmentPLC settings.zip (2340 Downloads) |
Be creative while inventing ideas and be disciplined while implementing them... :) |
|
This contribution was helpful to3 thankful Users |
6/24/2013 6:12 AM | |
Posts: 93 Rating: (13) |
Dear Friends, I would like to divert the disussion from internet based solution to GPRS/GSM based solution. Please visit siemens website of telecontrol solutions. It is great option to connect remote plcs where internet access is a problem. Best regards.. |
7/20/2015 9:17 PM | |
Posts: 1 Rating: (0) |
Dear All, Plz help me out: As we get access of S7 PLC 1200 through internet. How can i communicate CPU 315 2PN/DP through internet via router. Can i use same process as mentioned for s7 1200 communication by Mr. Marinkovic into earlier posts. I just tried to access to s71200 over internet and web server works great!!!! I sugest the following procedure: Step 1. Create a web server application and download it to S71200 Step 2. Testing web server application in LAN
Example: IP address of my PLC is 192.168.0.12 (Subnet mask 255.255.255.0., Router 192.168.0.1) I type in URL tab: http://192.168.0.12
Step 3. By Static IP address from your Internet provider,
Step 4. Router settings
(My router settings in attachments) Step 5. Remote testing
(80 - port number) |