Please help me, How to communicate 2 plc 315-2DP with CP lean both. Please provide step by step configuration and programming.. Thank yo so much Regards ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 2/22/2017 2:54:12 PMNew subject after splitting |
|
2/22/2017 2:51 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi, have a look in this manual on page 95. CPU-CPU Communication with SIMATIC ControllersAll possible communication between 2 S7-300 are mentioned there: as you see, it is only possible with Open User Communication and the T-blocks. hope this helps, regards, |