1/31/2021 6:02 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, Please refer below FAQ may help you. How should you configure the encoder settings in the TO ...Set PPR = 1048576 |
Last edited by: PISCEAN 2010 at: 01/31/2021 07:05:51Last edited by: Jen_Moderator at: 02/01/2021 09:54:14Optimized link. |
|
2/13/2021 3:59 PM | |
Joined: 1/17/2013 Last visit: 5/22/2024 Posts: 1082 Rating: (6) |
Dear PISCEAN 2010, Thank you for your one information. How about other value Fine resolution ? Gn_XIST2 ? Data width of absolute value without fine resolution ? And encoder mode Endat / SSI ? How can I calculate these value and how to select mode ? Best Regards, Vorapob |
Best Regards, |
|
2/14/2021 4:05 AM | |
Joined: 1/17/2013 Last visit: 5/22/2024 Posts: 1082 Rating: (6) |
Dear PISCEAN 2010, I try to put PPR = 1048576 but the drive has fault standstill. When I try to put PPR = 4096 it not fault but it has warning 20025 : Inconsistency between the TO and the drive/encoder configuration (category.5,additional information : 1, reason: 212) I don't know the exactly these value how to enter? Can someone help me ? Best Regards, Vorapob
|
Best Regards, |
|
2/23/2021 12:21 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, Please refer SINAMICS S120 Commissioning Manual with STARTER chapter 3.13 which explain detail information about configuration of encoder. HTH |
Last edited by: Jen_Moderator at: 02/24/2021 07:49:47Optimized link. |
|