Joined: 9/27/2006 Last visit: 11/11/2024 Posts: 12293 Rating: (2691) |
Hello APires; That is a correct configuration for the addressing on one side of the DP/DP coupler (slave #1). Remember that on the other side (slave #2) the order of the I/O must be reversed (keeping the same size per slot), i.e. start with the 64-byte inputs in slot 1, then the outputs in slot 2. Look at the screenshot below, taken from this FAQ document: DP/DP Coupler: how to configure it? https://support.industry.siemens.com/cs/ca/en/view/19281019 Hope this helps, Daniel Chartier |