Could anyone explain me how do I setup to read the voltage and current values of a Danfoss FDC302 inverter on a S7315 clp? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 4/20/2019 12:59:57 PMNew subject after splitting |
|
4/20/2019 12:35 AM | |
Joined: 9/27/2006 Last visit: 10/12/2024 Posts: 12287 Rating: (2685) |
Hello tecrmb; This is explained quite well, in this (short) manual from Danfoss: Siemens S7 PLC and FC 300 Profibus – Danfoss files.danfoss.com/download/Drives/MN33A102.pdf As you can see from the screenshot belopw, when you start configuring the drive you should select a PPO_ telegram that allows for a number of register values to be exchanged on top of the standard Control word and (Speed) Reference word. PPO5 for example gives you 4 Parameter channel words (that you do not need for the moment) and 6 Process channel words, the Control Word, the Reference and 4 extra registers you can associate with drive parameters as shown in the right side of the screenshot. Select the parameters you want to read (voltage, for example) and link them to P915/3 ... P915/6, as shown. They will then be transferred cyclically to the PLC during the Profibus transmission in the adresses associated with PCD 4 ... PCD 6. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 4/20/2019 1:12:11 AMLast edited by: dchartier at: 4/20/2019 5:11:27 PM |
|
4/20/2019 11:53 PM | |
Joined: 12/24/2016 Last visit: 6/28/2024 Posts: 9 Rating: (0) |
Thanks my friend! |