5/19/2020 9:57 PM | |
Joined: 3/30/2020 Last visit: 9/30/2024 Posts: 4801 Rating: (984) |
Hey. Normally it is good enough just to ignore the slave that is not giving a response and start the conversation with the next slave. It can happen that no slave is giving any feedback. In that case you can retrigger the MB_COMM_LOAD instruction. Take care that if you need to reinitialize the communication it is best not to repeat the process every cycle. Repeat the cycle every 5s, for example. Do not loose sight that the status feedback from the communication instruction will lead you to what actions you should be taken. Not all error codes need the same response. Are these notes clear? Late addition Disclaimer: I have not looked at it in detail. |
Last edited by: qwazee at: 05/19/2020 22:06:59Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|