1/22/2014 11:01 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
Hello, If your sensor is connected to the analog card directly you don't need FC105, just convert the analog value to Real and devide by 10.0. If some kind of converter is used and you have mA or voltage signal, have a look at attached pdf. Regards, Marcjan AttachmentFC1-scale-unscale.pdf (3640 Downloads) |
Problem solved? |
3 thankful Users |
1/22/2014 11:21 AM | |
Posts: 23 Rating:
Hi, I havereceived RTD value at PIW13 then what program i have to write to convert this analog value into real value. |
1/22/2014 11:39 AM | |
Hello, Have a look at attached pdf. Regards, Marcjan AttachmentFC1_rtd.pdf (2794 Downloads) |
Problem solved? |
3 thankful Users |
1/23/2014 3:40 AM | |
Joined: 10/7/2005 Last visit: 7/30/2024 Posts: 3013 Rating:
Hello Aashish the thread how to start an analog programmingto which you originally appended your question also contained answers that provided you with link to SIMATIC S7-300 SM331;AI 8x12 Bit Getting Started Part 2: Voltage and PT100. On that link you will not only find a nice pdf but also an example program (note the floppy disk icon with "Info" next to it). I hope this helps |
Cheers |
4/16/2015 12:18 PM | |
Joined: 9/1/2005 Last visit: 7/29/2024 Posts: 4104 Rating:
new question published by hamedamoula is split to a seperate thread with the subject convert analog entries to real
Best regards |