4/21/2012 4:06 PM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating: (272) |
it is must 4 H-system. |
VANDE MATARAM..... |
4/21/2012 4:27 PM | |
Joined: 5/28/2008 Last visit: 9/5/2024 Posts: 4515 Rating: (839) |
Hello, We have two Possible answers:
Hope this explanation helps. |
This contribution was helpful to1 thankful Users |
4/21/2012 4:42 PM | |
Joined: 10/7/2005 Last visit: 9/6/2024 Posts: 3018 Rating: (1054)
I'm sorry Ayman, but this advise is somewhat misguided. Apart from the fact that youwill still need bus modules for the Y-link itself, putting an ET200M behind a Y-link does a.) requires GSD file based configuration of the ET200M (Step 7 will - for good reasons - NOT allow you to drag in an Metadata based ET200M from the "normal" HWcatalogue) and b.) will cost you more all up in hardware and c.) does really NOT make any sense at all. |
This contribution was helpful to2 thankful Users |
4/25/2012 5:54 PM | |
Posts: 947 Rating: (45) |
Hi! Et200S support hot swapping, therefore you can build not H-system with hotswapping property. |
4/26/2012 6:13 AM | |
Joined: 8/18/2009 Last visit: 6/17/2024 Posts: 548 Rating: (33) |
Dear gre_m, As per my knowledge only ET200M support H-system, so in this matter(H-system) no ET200S we can take. |
Rajkiran Patil |