5/2/2021 4:20 PM | |
Joined: 9/21/2012 Last visit: 6/27/2024 Posts: 3980 Rating: (451) |
Why in earth would you need an .EDS file? That will not solve your problem... |
5/2/2021 5:34 PM | |
Joined: 9/27/2006 Last visit: 6/27/2024 Posts: 12264 Rating: (2672) |
Hello Blanco; I have a feeling that Hati and wizard are presenting you with good advice. If you look in the module's manual (available in various languages, but unfortunatey not in Portuguese) you will find no mention of a need for EDS files. Where did you read about that ossibility? If I were you I would concentrate more on the fact that all your input LEDs are active on these modules, in your screenshots, as well as at least one diagnostic LED on one of the F-DI modules.. There appears to be a configuration/parameterization error that does not allow the modules to become active. Look up the information on the parameters that must be set in the following link: - SIMATIC ET 200SP Digital input module F-DI 8x24VDC HF https://support.industry.siemens.com/cs/ww/en/view/78589499 Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
5/4/2021 8:54 PM | |
Joined: 5/11/2016 Last visit: 9/5/2022 Posts: 18 Rating: (0) |
yes, i asked for siemens. |
Blanco Automação |
|
5/5/2021 12:45 PM | |
Joined: 9/27/2006 Last visit: 6/27/2024 Posts: 12264 Rating: (2672) |
Hello Blanco; As per the msnual's documentation, the address range is fixed, and based on the hardware configuration. https://support.industry.siemens.com/cs/ww/en/view/78589499/46420703499 Hope this helps, |
Last edited by: dchartier at: 05/05/2021 12:46:27 |
|