Dear Sir, we want to use control in field function in FF base PCS7 system. For that purspose Host should support with PDM and specified designed faceplate. I want to know is there any specific tool or block available for Control in field option in PCS7?? |
Last edited by: HITUL007 at: 12/1/2014 6:28 AMJust want to know how to configure "Control in field" option in PCS7?? Last edited by: CS Moderator at: 12/1/2014 1:25 AMsplitting |
|
12/2/2014 1:18 PM | |
Joined: 2/14/2012 Last visit: 9/26/2024 Posts: 31 Rating: (10) |
Hello HITUL007, please check the application example regarding configuration of FOUNDATION Fieldbus H1 (FF) with SIMATIC PCS 7. There you can find a lot of information andan example how to configure a local display using control in the field functionality. Please checkthis example http://support.automation.siemens.com/WW/view/en/64329637. Hope I could help you |