3/28/2016 7:36 PM | |
Joined: 3/28/2015 Last visit: 8/25/2024 Posts: 721 Rating: (213) |
Hello, Kindly have a look at the attached file. |
Eng.Mohamed Ibrahim |
|
3/29/2016 5:57 PM | |
Joined: 3/28/2015 Last visit: 8/25/2024 Posts: 721 Rating: (213) |
Hello, Post a screenshot of it. |
Eng.Mohamed Ibrahim |
|
3/29/2016 6:38 PM | |
Joined: 2/10/2016 Last visit: 6/13/2024 Posts: 115 Rating: (0) |
here is the screen shot |
3/29/2016 6:41 PM | |
Joined: 2/10/2016 Last visit: 6/13/2024 Posts: 115 Rating: (0) |
and when i enter (time shift) this screen appears to me and only numbers are possible to be typed in this screen. |
3/29/2016 7:20 PM | |
Joined: 3/28/2015 Last visit: 8/25/2024 Posts: 721 Rating: (213) |
Hello, I recognize that you ask about Basic Panel So this option is not available and you need to do the following method: How do you synchronize the time of the HMI Basic Panel with an S7-1200 PLC? The method in the previous attached file can be applied to the following Panels: KTP400 Comfort KP400 Comfort TP700 Comfort KP700 Comfort TP900 Comfort KP900 Comfort TP1200 Comfort KP1200 Comfort TP1500 Comfort KP1500 Comfort TP1900 Comfort TP2200 Comfort Kindly have a look at the following topic: |
Eng.Mohamed Ibrahim |
|
This contribution was helpful to2 thankful Users |