Hello Davinder; Please give us more information on the installation of this flowmeter in your application. Based on the information available on the following link, vertical line installationwithout a grade can lead to an "empty pipe" situation, where the flowmeter is not able to detect a (relatively) low flow. Both electrodes of the flowmeter must be in contact with the medium at all times when taking measurements, see the attached file. SITRANS F Electromagnetic Flowmeters SITRANS F M MAG 5100 W Hope this helps, Daniel Chartier |