8/2/2022 9:10 AM | |
Joined: 8/3/2009 Last visit: 6/14/2024 Posts: 13030 Rating: (1660) |
Hello goudarzi91 do you mean shared device functionality? https://support.industry.siemens.com/cs/ww/en/view/109741600 Bye Murof |
If this Information really helps, you could use the Rate function |
|
8/5/2022 9:56 PM | |
Joined: 5/11/2022 Last visit: 6/9/2024 Posts: 59 Rating: (0) |
hi i'm talking about using inputs and outputs at the same time. two plc-1500, two et200 actually when the first plc has fault, the second plc read and write on inputs and outputs of et200 that assign to first plc |
8/5/2022 10:26 PM | |
Joined: 9/27/2006 Last visit: 6/14/2024 Posts: 12260 Rating: (2671)
|
Hello goudarzi; If I understand your situation correctly, i could be that yur solution might be a redundant pair of CPUs, in which the standby CPU is able to use the same I/Os in case the primary CPU fails. For the S7-1500 this would mean either a S7-1500R or a S7-1500H. The s7-1500H uses a fiber-otpic cable connection between the 2 redundant CPUs, allowing extremely fast data exchanges between the two CPUs, so the standby CPU is alwatys updated on the status of the shared I/O and program of the pimary CPU. https://support.industry.siemens.com/cs/ar/en/view/109754833 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 08/05/2022 22:59:51 |
|
This contribution was helpful to1 thankful Users |