5/23/2014 3:56 AM | |
Joined: 3/15/2011 Last visit: 10/26/2024 Posts: 134 Rating: (9) |
Hellow partners, I'm planning to use the MM 6SL3320-1TG41-3AA3to replace an inverter of SIMOVERT P system. My issue is that the DC link fault voltage of the system is configured to 1100V so i wan't to know the max allowable dc link voltage of this MM to chech compatibility. I couldn't find it in the engineering manual. Does anybody has this information?. BEST REGARDS Hi, Dc link threshold P2172 is hardware dependent ,one cannot exceed those limit,say mm has 800 VDC,allowable range is 90 % of this .you can't exceed this threshold value,otherwise drive may get damaged, hope it helps
Attachmentmm_dc_threshold.pdf (275 Downloads) |
This contribution was helpful to1 thankful Users |
5/23/2014 4:22 PM | |
Posts: 12 Rating: (0) |
Thanks for the answer. I think de information you sent is for MM440 and i'm planning to use SINAMICS S120 with motor module (MM)6SL3320-1TG41-3AA3. |