Max IO?? Max Rack?? my clarification in below link (all photo on one link) https://drive.google.com/open?id=1yaFGnMqnKVmlyFNbp1l4xuQ3kbBAEQ2M attached photo is one of my clarification ***updated 27/1/2020, 5:00 AM UTC*** I found answer one of my question The SIMATIC ET 200MP is a modular and scalable I/O system with IP20 degree of protection for universal use, and offers the same system advantages as the S7-1500. The SIMATIC ET 200MP permits extremely short bus cycles and very fast response times, even with large quantity structures. SIMATIC ET 200MP consists of the following components:
|
Last edited by: genious2015 at: 01/27/2020 03:53:18Last edited by: genious2015 at: 01/27/2020 05:57:20 |
|
1/26/2020 8:22 PM | |
Joined: 9/9/2014 Last visit: 7/11/2024 Posts: 246 Rating: (40) |
Hello, The information in the picture is correct, why? It's simple: You have 2048 bytes on the process images (adress area) for inputs/outputs. This is in theory - 2048 bytes * 8 bits = 16384 digital inputs or outputs Or 2048 bytes / 2 words = 1024 analog outputs or inputs. ********************** Why in theory, but because usually - rarely, someone fills the whole image of the process - secondly -> it is better to leave a margin for inputs and outputs, about 15 percent. ********************** İs it possible to use 8 Modules with 32 Inputs /Outputs Each? If I answered your question, please close the topic and rate. |
Best Regards |
|
This contribution was helpful to1 thankful Users |
1/27/2020 3:44 AM | |
Joined: 8/31/2016 Last visit: 4/29/2024 Posts: 89 Rating: (1) |
Thanks for your reply Photos from data sheet, ****There are other photo on link in main topic*** |