11/20/2014 4:09 AM | |
Joined: 1/9/2012 Last visit: 3/28/2024 Posts: 40 Rating: (5) |
Hi AutoGen_6415, What is your requirement? Modbus TCP Server or client. So firstrole (Modbus TCP client/server)needs to be clear. Then you can selectblocks accordingly. Since Modscan ≈Modbus TCP client and Modsim ≈Modbus TCP Server, If you have made CPU as server then itmay not work with Modsim. |
11/20/2014 7:45 PM | |
Posts: 10 Rating: (0) |
I thought that I made it clear. Sorry if not, but the CP443-1 is a Modbus/TCP server. |
11/21/2014 8:49 AM | |
Joined: 10/3/2008 Last visit: 5/22/2024 Posts: 957 Rating: (123)
|
Hi, if multiple clients want to connect to the server, you need multiple Modbus block instances. Wüstenräuber |
11/24/2014 7:22 AM | |
Joined: 1/9/2012 Last visit: 3/28/2024 Posts: 40 Rating: (5) |
Hi, |
11/24/2014 10:01 PM | |
Posts: 10 Rating: (0) |
The error I see says that it is not parameterized, but I know that it is parameterized. |
11/25/2014 7:00 PM | |
Posts: 10 Rating: (0) |
Getting Modbus Exception from Slave Device (TCP Server) |
11/25/2014 9:46 PM | |
Joined: 10/3/2008 Last visit: 5/22/2024 Posts: 957 Rating: (123)
|
Hi, then the client sent a telegram, which the server can't handle. Check the addresses in server. Wüstenräuber |
11/26/2014 6:45 PM | |
Posts: 10 Rating: (0) |
This is the latest data from the CPU still with no ability see data written by the client. |
11/26/2014 9:11 PM | |
Posts: 10 Rating: (0) |
Here is the IDB1541
Attachmentdb1541.zip (264 Downloads) |
11/26/2014 9:14 PM | |
Joined: 10/3/2008 Last visit: 5/22/2024 Posts: 957 Rating: (123)
|
No, not the offline IDB! The online IDB with the current values. |
11/26/2014 9:30 PM | |
Posts: 10 Rating: (0) |
Sorry. Here is the online IDB. AttachmentTrasport.zip (307 Downloads) |
Follow us on