2/18/2012 10:09 AM | |
Joined: 8/18/2009 Last visit: 6/17/2024 Posts: 548 Rating: (33) |
Please tell me which current value we should consider during panel designing... |
Rajkiran Patil |
|
2/18/2012 10:29 AM | |
Joined: 5/28/2008 Last visit: 10/7/2024 Posts: 4515 Rating: (839) |
Hello, According to technical specifications in thislink, input current at 230 VAC is 0.5 Amps. So, if you will use this voltage selection, you have to use a MCB with rating greater than 0.5 A. 0.63 or 1 A will be fine. And for inrush current, it is stated in the technical specifications 63A;Full width at half maximum 1 ms, and of course MCB should not have enough time to trip (only 1ms). Hope this helps.
|
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |
2/21/2012 5:55 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (308)
|
Hello RAJKIRAN, For heat calculation you should use the power loss which actually is the heat dissipation. The power loss of6ES7407-0KA02-0AA0 is 20 W. Best regards. H-H
|