3/5/2009 3:26 AM | |
Posts: 78 Rating: (0) |
MeasureInput function is effective . but it need to FastIO in the board or other TM module |
3/10/2009 4:42 AM | |
Joined: 5/12/2006 Last visit: 5/2/2024 Posts: 22243 Rating: (2981)
|
Hello, when you set p680 = 1 you use DI X122.8 for Input, so the adress for the TO is 307.1 (startadress of ControlUnit + Offset fpr DI X122.8). Refer this FAQ for more informations: http://support.automation.siemens.com/WW/view/en/29063656 Regards Christoph |
8/11/2009 8:14 AM | |
Posts: 116 Rating: (7) |
Hi, see my answer ... but the 'countermeasuredvalue1' does not raise. --> that's for global measuring inputs and cyclic measurements. Local measuring inputs with non cyclic measuringhave a hand shake; you always have to enable the measuring input after a measurement. Global measuring inputs with cyclic measuring have no hand shake --- so you have a counter to determine, it you have a new measurement. Don't use local measuring inputs with cyclic measuring! (that's a mistake in the FAQ release V1.1, quoted below) Now I have it working, but is working as a local or a global measuring input ? If you use TO measuring input with - a measuring input number --> local measuring input - a hardware address --> global measuring input see also http://support.automation.siemens.com/WW/view/en/29063656
|
8/14/2009 1:23 PM | |
Posts: 116 Rating: (7) |
Hi, Difference is that in the configuration screen of the measuring input I select 'local measuring' but also in the configuration data in the expert list I have to fill in the log address (as it should be in for global measuring) --> HW--Address is not relevant for global measuring inputsOn Sinamics level I only set p488 to the measuring input and not 680 of the CU (as for global measuring). Fact is that in my Profibus telegram I have put encoder 3 on the place of encoder 1 (you can only transfer 2 encoders to Simotion, and I don't use Sinamics encoder 1 (motor encoder) in Simotion, but I need Sinamics encoder 3 in Simotion as value for my external encoder object where I have the measuring input). I'm not sure if this would work?!?! alternative: 3rd encoder as PROFIBUS encoder with PROFIdriveI only use the non-cyclic enabling of the measuring input (as for local measuring) but the enable is my example connected constantly to a true value, so I can see my countervalue raising whithout explictly acknowledging a handshake. counterMeasuredValue is for "cyclic measuring" and "cyclic measuring" is only for global measuring inputsI guess, that you use cyclic measuring with local measuring inputs --- don't do this!Note (see Manual Output Cams and Measuring Inputs)Cyclic measurement is only possible with global measuring inputs at the inputs TM17 High Feature, SIMOTION D onboard and C240 (B1-B4). Question was, will this in fact work correctly towards the measured values No!, and do I have to fill in the compensation times as for global measuring inputs? Normally not for local measuring inputsIf measurements have to be performed with "very high" accuracy or the dead times caused by the filter time constant and delay times from the transmission line, BERO, converter, contacts, etc. cannot be ignored, it is recommended a machine-specific determination of the dead times that really occur, through measurements or series of measurements. Measurements with velocitydependent displaced measuring results is anindication the dead times have not been compensated or incorrectly compensated.The procedure for "empirical/metrological determination" of dead times is similar to the procedure for determining the dead times for the output cams (see Output Cam and Measuring Input Function Manual, Chapter "Determining actuation times for output cams (dead time compensation)")Also, if I would define it as global, is that possible, because I have no explicit telegram 391 but one based on it (only the acknowledgebit has been added)? Don't change 39x to free telegram and use global measuring inputs! I you switch to 39x, select with cu.p728 an input, select with cu.p680 an measuring input and then proceed a HW config adjustment, a fastIO config is generated (= internal configuration information that SIMOTION knows, here you have assigned a global measuring input for the drive --- this also works with CUs/CX32) Change filetype of upload from jpg to rar to unpack it. I can't open RAR
|
Last edited by: Jerry at: 8/14/2009 1:26 PM |
|