5/15/2019 2:55 PM | |
Joined: 9/27/2006 Last visit: 5/2/2024 Posts: 12257 Rating: (2666) |
Hello Nkosi; Here are basic documents showing control of the MM420 drive from the digital inputs (terminal strips) and the BOP. If you want to control from the BOP, parameter P0700 must be set at "1", for digital input control parameter P0700 must be set to "2". In the first document, examine the tables in section 3.5.5.2, and section 3.6 to see how digital inputs of the drive can be selected and attributed functions. Operating Instructions: MICROMASTER 420 0,12 kW - 11 kW https://support.industry.siemens.com/cs/us/en/view/24523400 MICROMASTER 4 (MM4): 2-wire 3-wire control (can be used for PLC control as well) https://support.industry.siemens.com/cs/us/en/view/5800810 MM420: start a motor with digital input Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 05/15/2019 14:56:22 |
|
This contribution was helpful to1 thankful Users |