Hello. Please request for my English. Please tell me whether you can configure this drive for 6 or 8 of the PKW.
|
8/7/2012 10:06 PM | |
Joined: 9/27/2006 Last visit: 10/17/2024 Posts: 12289 Rating: (2687) |
Hello jurik; Welcome tothe the Siemens A&D forum. Profibus communications with a MM4 drive uses 2 areas: - cyclic exchanges for process data (Control word, speed reference...): the PZD registers; - acyclic exchanges for parameters read/writeusing the PKW registers. The PKW area is composed of 4 registers that you use to read or write any parameter available on the drive. See the attache screencapture (from hwe MM4 Profibus optional board manual): Operating Instructions: MICROMASTER PROFIBUS Optional Board |
Last edited by: dchartier at: 8/7/2012 10:08 PM |
|
1/11/2016 12:42 AM | |
Joined: 9/1/2005 Last visit: 10/14/2024 Posts: 4109 Rating: (195) |
New question published by mubbashir is split to a separate thread with the subject Response MM4 / CU240 => PROFIBUS / PROFINET. Best regards |