6/1/2011 1:04 PM | |
Joined: 10/3/2010 Last visit: 9/9/2025 Posts: 1568 Rating:
|
CPU type (984, Compact, Quantum, Momentum, Premium, Micro) is all about Modicon devices, as they stand for Modbus in general. There's no option to choose other kinds of Modbus-capable devices but if you're lucky, one of these might just work as well for your Wago PLC. Just try. more info in ModbusTCPIP.pdf or ModbusTCPIP.chm WinCC Information System->Communication->Modbus TCP/IP try to follow this example and change CPU type if it won't work http://support.automation.siemens.com/GB/view/en/37885119 IP-address is the one from your WAGO Slave-address is the Modbus slave number from your WAGO (usually between 1-254) |
Last edited by: SteBo at: 6/1/2011 1:12 PMB r g d s , |
|
6/1/2011 1:42 PM | |
Posts: 691 Rating:
|
Hi AEnes I also don't think that you will be able to communicate your PLC Wago 750-841. However you can read the data through S7 CPU with Ethernet CP Module |
6/1/2011 2:09 PM | |
Joined: 10/3/2010 Last visit: 9/9/2025 Posts: 1568 Rating:
|
standard Modbus TCP/IP port is 502 |