8/12/2021 1:08 PM | |
Posts: 2 Rating: (3) |
I understand your problem! You are just changing the slave id/unit but you have to change the port number on the same IP. ie: 10.10.20.30:502 is your main PAC-4200 access and 10.10.20.30:17002 to access Slave-1 if the RS485 bus is connected to the "MOD1" slot. here is the official document link: https://support.industry.siemens.com/cs/attachments/34261595/manual_pac4200_en-US_en-US.pdf?download=true see the page number: 41 Although it's too late to answer but it may help someone! Thanks, Aman Attachmentmanual_pac4200_en-US_en-US.pdf (531 Downloads) |
Last edited by: Jen_Moderator at: 08/12/2021 13:46:26Added PDF as an attachment. |
|
This contribution was helpful to2 thankful Users |
7/28/2023 7:56 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by Vinizuca is split to a separate thread with the subject Modbus Rtu over Tcp via Pac4200: can read the PAC4200, but slaves return the same value as the PAC4200. . Best regards |
Follow us on