3/15/2017 3:06 PM | |
Posts: 6 Rating: (1) |
Sorry Towome for the late reply... You can find a tutorial for MODBUS TCP communication between 2 CPU S7-1500 by following the link : modbus-tcp-communication-between-two-s7-1500-cpus My case was between a S7-1500 (client) and a Schneider TSX57 CPU (server). From the Schneider side, there is nothing to do (not even I/O scanning). Everything has to be made on the Siemens side : follow the tutorial, and be careful to the following parameters of the MB_CLIENT block : Ex 1 : write 6 registers to %MW1720 Ex 2 : read 3 registers from %MW1710 The parameter CONNECT contains all the parameters for the communication. Here are the ones you have to care about : I hope this will be helpful for someone else... Renaud MARY |
3/15/2018 12:39 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (174) |
New question published by lekmetochdezak is split to a separate thread with the subject Question concerning the RemoteAddress - can't alter the values of the addr[1-4. Best regards |