I want to modify it temporary, the programs like this, the target is M91.3 & Q6.7 . I want to keep the variables target is true although the input changed. |
3/1/2021 9:08 AM | |
Joined: 7/9/2015 Last visit: 11/19/2024 Posts: 4028 Rating: (603)
|
Hi, with S7-300 and Simatic Manager you can also use triggers. Please check manual chapter 20.7 Modifying Variables and 20.8 Forcing Variables SIMATIC Programming with STEP 7Regards,Towome
|