9/19/2019 7:22 AM | |
Joined: 9/9/2015 Last visit: 6/7/2024 Posts: 727 Rating: (270) |
Please see my reply above. When you deliver the panels or the system, the Input and Output modules should already be check properly. For the DI modules, to confirm the module is working properly, disconnect the field wiring, do a short circuit test to see if it is functioning normally. I do not think it is a programming issue but a local panel design issue. Hope it helps. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
9/26/2019 10:34 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (216) |
Hello PLC2011, the problem is that you use the operating mode "Local mode". This operating mode is used for motors, valves and dosing units. The control settings are made directly or via a control station that is located "locally". In addition, you can set different control strategies with the parameter LocalSetting. Please check the manual PCS 7 Advanced Process Library in the section State graph of the operating modes and Local mode. With regrads |