Hello Tomy; You have a CPU 315-2DP, but its MPI port is damaged... What about the Profibus port? You can use it for downloading/uploading even if it used to communicate to distributed I/O stations, if you have a piggy-back Profibus connector on that port, so you can connect your programming cable (see the attached screenshot below). By the way, what interface are you using, a USB-PC adapter, a CP 5612A2... If there is a Ethernet CP 343-1 on the rack, you could also use it to perform your downloads from your programming computer. Have a look at this document that summarises the steps for connecting to a Siemens PLC. http://www.plcdev.com/book/export/html/597 Hope this helps, Daniel Chartier |