Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, User needs special software & hardware to read/write/modify/copy etc Siemens PCMCIA cards. For more information please read attached sheet. I don't think you need this software. Just get an equivalent NCU card, fitt it, plug in PCMCIA card & reload the back up. Your problem should get resolved. If PCMCIA card it faulty, contact your nearest service support for further support. HTH. AttachmentC:\Documents and Settings\ntguest\Desktop\SINUCOM FFS.pdf (249 Downloads) |
Last edited by: PISCEAN 2010 at: 7/24/2014 7:06 AM |
|
This contribution was helpful to1 thankful Users |
8/1/2014 6:11 PM | |
Posts: 12 Rating: (0) |
FINALY the problem is resolved. After some really bad luck with the 2 NEW NCUs and the software from the machine manufacturer we finaly get a 6 on the 7th element display, The PCMCIA card directly from siemens payed off, and the onld NCU is booting and we managed to start the machine. We also changed the power supply for the NC, aparently that was causing some problems also, but maninly it was the PCMCIA card. We also reinstaled the OS on the NCU. Thank you SIEMENS! Thank youPISCEAN 2010 Thank youAutoGen_481139 topic can be closed. |