Industry Online Support
Technical Forum
6/29/2010 12:37 PM | |
Posts: 2964 Rating: (481) |
Hello... NCU series .3.4.5 series differences are in the Processor-CNC memory-PLC CPU-PLC memory (.3 series PLC 315-2DP) (.4 series PLC 314C--2DP) (.5 series PLC 317-2DP) You can refer the same in DOCON WEB Startup-Guide 840D/810D for your immedaite reference you can refer this document. When you are replacing NCU 571.3 to 571.5 >Ensure you have your NCPLC archive backups properly >Simatic Step7 backup. >When you arereplacing with 571.5, do not loadarchive backups first. > Open a new project take aPLC upload through simatic manager (FB15,DB1) blocks will be copied >Open your old project COPY all the blocks except (FB15,DB1) and paste it in your new project > Compile and check any errors are present if no errors download the same. > Load your NC Archive alone >Now the machine should be in working condition > Create a fresh NC PLC archive backup. > If you have your older PLC archive delete it. Check it out.... Ekalavya Attachment-3-4-5 NCU series.pdf (294 Downloads) |
This contribution was helpful to3 thankful Users |