12/6/2019 1:20 PM | |
Posts: 14 Rating: (1) |
Hi, Very helpful suggestion. Havent tried to ping so I'll get right on it... |
12/6/2019 3:46 PM | |
Posts: 1283 Rating: (105) |
What is your IP of the computer with TIA, PLC IP and WinCC Advanced IP? |
This contribution was helpful to1 thankful Users |
12/6/2019 3:46 PM | |
Posts: 1283 Rating: (105) |
In WinCC advanced, did you set the proper PG PC interface card? |
This contribution was helpful to2 thankful Users |
12/6/2019 4:23 PM | |
Joined: 4/24/2006 Last visit: 4/26/2024 Posts: 8616 Rating: (1147) |
Hello, Have you seen this link: Best regards, Wizard |
This contribution was helpful to1 thankful Users |
12/9/2019 8:27 AM | |
Posts: 14 Rating: (1) |
Hi, Thanks for answering The IP's are identical save for the last number where I have .98 (PLC) .141 (PC station) .13 (Server running TIA portal) |
12/9/2019 8:33 AM | |
Posts: 1283 Rating: (105) |
PG/PC interface setting in control panel? |
This contribution was helpful to1 thankful Users |
12/9/2019 8:52 AM | |
Posts: 14 Rating: (1) |
@Jay: I found the PG/PC interface settings and have attached a screenshot. I'm not familiar with this so I don't know if this is OK or not... Comments? |
12/9/2019 9:09 AM | |
Posts: 14 Rating: (1) |
So, from the pull down menu "Access point of the application"Should I change it for both lines? MPI (WinCC) and S7ONLINE (STEP 7) or just the MPI (WiinCC) line? |