Joined: 2/1/2010 Last visit: 10/3/2024 Posts: 150 Rating: (71) |
Are you sure the SFC is not being set to auto programmatically from CFC or another SFC? That's what it looks like could be happening. Your user input will always be overridden if you have something writing to the nub instead. Even SFC charts still have nubs like SFC type, you can see them if you 'open external view' and check link/SFC access on the nub there. |
If my post helped you, please rate. Thanks. |
|
8/13/2020 4:31 AM | |
Joined: 9/9/2015 Last visit: 10/8/2024 Posts: 727 Rating: (278) |
Ensure not to "Lock" the Auto/Manual by linking the "auto" input and fix it at "1" in external view of SFC. Then you will be able to set the sfc to manual in HMI. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
8/13/2020 9:09 AM | |
Joined: 9/9/2015 Last visit: 10/8/2024 Posts: 727 Rating: (278) |
Then it will be even easier. Please right click at your sfc in external view, set the "EnMAN" to 1. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
8/13/2020 12:40 PM | |
Joined: 9/9/2015 Last visit: 10/8/2024 Posts: 727 Rating: (278) |
It sound interesting. Could you share me your block properties configuration? all the IO properties. Let me set up one and check it. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
8/14/2020 2:17 PM | |
Joined: 2/1/2010 Last visit: 10/3/2024 Posts: 150 Rating: (71) |
BitRidder It appears these SFC have already run through at least 1 time, maybe more, so far. Are you able to force the transition true (by CFC logic manipulation or by the process progress) to make it carry on to the next step or are all the SFC permanently stuck in their current step even if the transition conditions are true? How about using the external view nubs to force a state change? |
If my post helped you, please rate. Thanks. |
|