Follow-up: After adding error trapping to the script, we found that the following error was raised: 2147467259 [Microsoft][ODBC Driver Manager] The specified DSN contains an architecture mismatch between the Driver and Application This seems to indicate that WinCC Flexible uses the 32-bit scripting engine, combined with a 64-bit ODBC driver, which fails (https://msdn.microsoft.com/en-us/library/ms712362(VS.85).aspx). After recreating the DSN with c:\windows\sysWOW64\odbcad32.exe (the 32-bit ODBC administrator), the script works fine again. |