7/31/2018 8:46 AM | |
Posts: 50 Rating: (0) |
i have two of these sensors mounted on the machine. is the pulse time 50us? the registration marks as around 7mm wide. thanks again, matty g Attachmentsensor.docx (133 Downloads) |
8/1/2018 8:23 AM | |
Posts: 50 Rating: (0) |
https://www.sick.com/ag/en/registration-sensors/contrast-sensors/kt5/kt5w-2p1116d/p/p169067 this is the sensor. Thanks again matty g |
8/3/2018 4:57 PM | |
Posts: 50 Rating: (0) |
Hi again, is the sensor information provided from the web page enough? cheers again matty g |
8/4/2018 10:42 AM | |
Posts: 50 Rating: (0) |
Hi, can you help me to use the same program design but with two high speed counters instead please? cheers, matty g |
8/5/2018 3:51 PM | |
Joined: 5/6/2010 Last visit: 10/13/2024 Posts: 1984 Rating: (278) |
Hello Matty, you can see in the attachment the suggestion (with two counters and comparation) for your program. The input filter with 50µs is ok, the pulse of your mark is nearly 1.68 ms. I hope that this suggestion is helpful. regards AttachmentHSC.zip (142 Downloads) |
This contribution was helpful to2 thankful Users |
8/5/2018 8:31 PM | |
Posts: 50 Rating: (0) |
Hi again, Thanks for the example! The counter isn't working when i force the inputs though? have i done something wrong? Cheers Matty G AttachmentLaser Prog.docx (127 Downloads) |