Hello, here´s my problem there´s an OP7 panel that shows the message Simatic OP7 V1.03 TTY Press (UP) V24 Press(DOWN) and before Simatic OP7 V1.03 Ready for transfer Do you think it lost its program ? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 4/21/2016 11:26:30 AMNew subject after splitting |
|
4/20/2016 8:01 PM | |
Joined: 3/28/2015 Last visit: 10/4/2024 Posts: 721 Rating: (213) |
Hello, I think the panel lost the program. |
Last edited by: Online Tech at: 4/20/2016 8:53:31 PMEng.Mohamed Ibrahim |
|
4/20/2016 8:06 PM | |
Posts: 8 Rating: (0) |
Problem is no backup available. This came in an old equipment |
4/20/2016 9:13 PM | |
Joined: 3/28/2015 Last visit: 10/4/2024 Posts: 721 Rating: (213) |
Hello, 1-If the designer gave you the backup of the program,you need the ProSave software to download the program to the panel. 2-If the designer gave you the configuration program,you need the Protool software to download the program to the panel and I prefer this because I can migrate it later. |
Eng.Mohamed Ibrahim |
|
4/20/2016 9:20 PM | |
Joined: 5/28/2008 Last visit: 10/12/2024 Posts: 4515 Rating: (839) |
In section 2.2 of this link the pin assignment of the cable that you can use to download to OP7. |
Ayman Elotaify |
|
4/20/2016 9:54 PM | |
Joined: 3/28/2015 Last visit: 10/4/2024 Posts: 721 Rating: (213) |
Hello, Kindly find the attached file. |
Eng.Mohamed Ibrahim |
|