2/27/2024 1:00 PM | |
Joined: 8/3/2009 Last visit: 9/30/2024 Posts: 13826 Rating: (1744) |
Hello drugo85 What do you mean exactly with OPC -DA ? Do you mean: - OPC Data Access (DCOM based)? -> NO, as the name says, DCOM Based needs a Windows OS To get access to a PLC with OPC DA (DCOM) you would need a PC Based OPC Server that accesses the PLCs with S7 communication like (LINK) - OPC UA DA(DataAccess)-> S71500 Support a direct OPC UA Client on the Controller (LINK) Bye Murof |
Last edited by: Murof at: 02/27/2024 13:01:30If this Information really helps, you could use the Rate function |
|
3/18/2024 1:57 PM | |
Joined: 8/3/2009 Last visit: 9/30/2024 Posts: 13826 Rating: (1744) |
Hello drugo85 so the classic PLCs do not have an integrated OPC Server/client, so you would need an OPc Server that can do S7 communication to get access to the PLC tags. If you have S7-1500 then you can use OPC UA Server and Client directly on the Server. If you have to access these PLCs from a OPC DA (DCOM based) Client then you can use this: https://support.industry.siemens.com/cs/de/en/view/109474300
Bye Murof |
If this Information really helps, you could use the Rate function |
|