12/19/2016 9:36 AM | |
Joined: 4/28/2015 Last visit: 3/23/2024 Posts: 3345 Rating: (375)
|
This Application Example shows how to use the SIMATIC IOT2000 as OPC UA Client using node-red
AttachmentOPC_UA_Client_node-red_V1.0.pdf (6986 Downloads) |
Last edited by: bergmanu at: 12/20/2016 1:25:08 PMchanged typing errors in the attached file Not working for IOT2050 support anymore from March 1st, 2024. |
|
This contribution was helpful to4 thankful Users |
2/28/2017 1:02 PM | |
Posts: 215 Rating: (6) |
It says on page 9 to add the NodeID of the required value. Where can I get that? |
2/28/2017 2:46 PM | |
Posts: 215 Rating: (6) |
I've checked the ID but I can't figure out, why the gauge is still showing nothing. I'm using PLCSSim Advanced 1.0, and the software should support OPC UA. |
2/28/2017 3:33 PM | |
Posts: 215 Rating: (6) |
Ok, here it goes: Furthermore: I activated OPC UA server on the PLC, the tag is checked as accessible from HMI/OPC UA, nodeID is copied from the exported xml file, IP adresses are right (S7 communication still works). Attachmentnode_red_opc.txt (1678 Downloads) |
Last edited by: JDarius at: 2/28/2017 3:39:46 PM |
|