Joined: 12/16/2018 Last visit: 5/23/2024 Posts: 2 Rating: (0) |
Hi Smith, I have a similar problem with communication OPCUA with Kepserver, I can browse tags from server but it does not read variables properly. I also checked the communication via UAExpert and it works fine. Can you write what was wrong with your configuration on the kepware side? Best regards Michal ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/03/2021 11:22:59New subject after splitting |
|
11/3/2021 2:26 PM | |
Joined: 3/28/2010 Last visit: 11/16/2024 Posts: 1074 Rating: (214) |
Two examples of the incorrect and the correct value readings are . . . .? |
11/4/2021 12:35 AM | |
Joined: 7/24/2014 Last visit: 12/4/2023 Posts: 392 Rating: (66) |
You can check the settings in the Kepware go for the settings in Subscription -> Update mode -> and change that from Exception to Poll and this got mine one working. I was not having sucess witht the tag quality, I wasnt having the bad tag value problem. Also check the address how you put in adderess. I have the format of ns=4;s=SIMOTION_PLCAddressVar_ib_00 and datatype as Default and Scan rate to 5000. the s in the address format is the tag name in the server and its type is String. Let me know if it works or not
|
Thanks and Regards |
|
This contribution was helpful to2 thankful Users |