4/28/2012 2:27 PM | |
Posts: 8946 Rating: (999) |
Please read this thread also: /tf/WW/en/Posts/72685#top |
4/28/2012 7:05 PM | |
Joined: 8/25/2011 Last visit: 10/2/2024 Posts: 29 Rating: (4) |
How are you measuring the speed?Howmuch variation are you seeing? |
4/28/2012 8:00 PM | |
Joined: 6/4/2008 Last visit: 10/10/2024 Posts: 1502 Rating: (324)
|
Hi Amit3545, As IBN-Service stated, you absolutely cannot make sense of drive output multimeter readings at most speeds, but even worse for low speeds. You definately need an ascilloscope here - then you can see the exact voltage output. If the motor is unstable, please confirm the motor is good by performing an insulation resistance measurement on the motor. If this is ok, I would recommend creating a backup of your drive parameters and then factory default the drive and start the basic commissioning with the simplest setup (This ensures no unexpected parameterisations are present) as follows: Enter your motor data correctly (Check for wiring configuration) P554=5 P573=8 P574=9 P443=58 Regards, Graeme
|